Does an rcd detect a neutral fault or is it just and earth / live fault ??
Also, would you run a separate earth with a 16mm or higher swa cable??

Thanks

Sav
 
Hi.

An RCD will operate upon sensing of an earth fault i.e line to earth or neutral to earth as it monitors the current flow between line and neutral. There is no overload protection, fuses and MCB's provide that.

As for seperate earths it depends on number of cores as the armour size varies with these too.
 
Last edited by a moderator:
Hi people,

Does an rcd detect a neutral fault or is it just and earth / live fault ??
Also, would you run a separate earth with a 16mm or higher swa cable??

Thanks

Sav

An RCD works on that it monitors what current goes down the live comes back down the neutral (single phase) if there is a difference between them of more than 30mA for a 30 mA RCD it will trip.

So if there is a fault between N & E it will trip.
 
Hi Lenny,
Thanks for the reply. So if say I was running a 16mm swa from a house to a storeroom supply, would you suggest running an extra, say 10mm earth for additional protection ??
An old boss of mine said there is no need to , but another guy said its best to as its over 10mm swa and to be within regs /readings. I cant find it in the BS7671 or OSG where it advises this.
Please help .
thanks again in advance
Sav
:eek:
 
Hi Lenny,
Thanks for the reply. So if say I was running a 16mm swa from a house to a storeroom supply, would you suggest running an extra, say 10mm earth for additional protection ??
An old boss of mine said there is no need to , but another guy said its best to as its over 10mm swa and to be within regs /readings. I cant find it in the BS7671 or OSG where it advises this.
Please help .
thanks again in advance
Sav
:eek:

Have worked on many sites where what ever it says in the regs a seperate CPC half the size of the main cable must be installed way it is going as sepecified by main site.
 

Reply to RCD question please in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
305
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
825
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
912

Similar threads

  • Question
That was my saying not long ago about TNS to PME system. I would be nice you can ring up the DNO, will the systems being up graded, there is a...
Replies
9
Views
2K
  • Question
One of those backlight Chinese testers may have helped that’s if the tester didn’t catch fire or electrocute you. LED TV Backlight Tester 12W LED...
2 3 4 5
Replies
68
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top