rcd rating is this suitable | on ElectriciansForums

Discuss rcd rating is this suitable in the UK Electrical Forum area at ElectriciansForums.net

Joined
Aug 9, 2012
Messages
77
Reaction score
14
quick question,
80a/30ma rcd protecting 5 32a circuits
2 ring mains
1 oven
1 shower
1 hob
ive been told the shower and hob need upgraded to 40a mcbs
is the rcd still suitable
one ring main supplys 4 bedroom sockets the other kitchen/living area with 7 sockets.
 

Attachments

  • [ElectriciansForums.net] rcd rating is this suitable
    16466604206083322662963800269300.jpg
    183.9 KB · Views: 47
i could cut the seal and find out....maybe the guy who says i need an upgraded mcb cut it open and sealed it again supply cable is500/1000v rated,im in a cupboard with crap glasses on.
i would not venture doing that ,is there two consumer units ,your post says
80a/30ma rcd protecting 5 32a circuits
2 ring mains
take a pic of the set up regarding the cu.
 
ive misread that last post from buzz I quickly read it and thought you asked for a picture of the cut out
and im on my way home now...sorry
The incoming fuse could be 100A, but most often they are 80A - the holder in all cases is rated 100A and the picture you posted only shows the standard fuse holder rating, there is nothing in the photo to confirm the actual fuse size.

So the question of actual load remains, in order to exceed 80A essentially the shower, all the Hobs and around 10A of rfc load would all have to be on together, if this is a typical house, I would think this would be very unlikely.

If it is someone running a home cooking business, with a few fan heaters around the place etc, and kids taking long showers etc; then they could be in excess of 80A.

I don't subscribe to the old style estimates for max demand in terms of lighting and ring finals, as we now distribute the loads over several circuits, not because of load, but for safety/security of supply.

The modern model of multiple circuits doesn't mean a corresponding increase in load, merely a distributed 'same' load
 
The incoming fuse could be 100A, but most often they are 80A - the holder in all cases is rated 100A and the picture you posted only shows the standard fuse holder rating, there is nothing in the photo to confirm the actual fuse size.

So the question of actual load remains, in order to exceed 80A essentially the shower, all the Hobs and around 10A of rfc load would all have to be on together, if this is a typical house, I would think this would be very unlikely.

If it is someone running a home cooking business, with a few fan heaters around the place etc, and kids taking long showers etc; then they could be in excess of 80A.

I don't subscribe to the old style estimates for max demand in terms of lighting and ring finals, as we now distribute the loads over several circuits, not because of load, but for safety/security of supply.

The modern model of multiple circuits doesn't mean a corresponding increase in load, merely a distributed 'same' load
Thanks for the reply,
In reply to a previous post the CU is a split load with a 100a isolator one half is protected by the rcd 3 x32 and now 2x 40 and the other half is 2x6a -lights 1x16a -boiler and 1x6 a smoke detectors
The premise is a flat leased on a serviced apartment type thing anything from 1 night to a year and more.
Im the maintenance man from Aberdeen (ex sparky) and have been down correcting all the c2's that a company found whilst they were carrying out EICR's for the building (25 flats)
What I have found strange though is that all 25 flats are identical yet not all of them have been flagged for having an mcb rated too low also whoever did the tests missed at least one FI,(didnt get all the work done I tested positive...whilst in weegie land so came home) one of the rings in the bedrooms is missing a leg and this is the second EICR done on these flats.
 
Last edited:
I thought the regs now say that the rating of the RCD must be equal to or exceed the sum of the ratings of all the MCBs it feeds, without diversity, OR, the rating of the upstream protective device must not exceed the rating of the RCD?
 
I thought the regs now say that the rating of the RCD must be equal to or exceed the sum of the ratings of all the MCBs it feeds, without diversity, OR, the rating of the upstream protective device must not exceed the rating of the RCD?
if thats right can it be applied retrospectively? that would mean an awful lot of rcds needing changed
 
if thats right can it be applied retrospectively? that would mean an awful lot of rcds needing changed

Regulations do not need to be applied retrospectively but if you are making changes then all changes must be made to current standards..

You could contact the DNO and ask them, I can't remember the exact section but Brian is correct, as standard now if fitting a dual RCD board which I tend to fit RCBO boards I would fit dual 100A type A RCD's, as if you cannot be sure what the size of the fuse is you should assume it is worst case scenario of 100A..
 

Reply to rcd rating is this suitable in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
257
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
739
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
721

Similar threads

  • Question
ok cheers for the help lads
Replies
7
Views
698
  • Question
A kettle boiling fish - thats your fault right there... or is it a red herring? :)
Replies
4
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top