Went to inspect a rented property the other day.

TNC-S, Consumer unit has RCD as main switch protecting all circuits. Not too keen on the idea of one RCD (16th edition install about 10 years old), but anyway that wasn't really my concearn. The RCD was only rated at 63amps and it had the following circuits connected:

45amp cooker circuit
4 x 32amp ring circuits
4 x 6amp lighting circuits

although the RCD didn't show any signs of burning out etc, I gave it a code 2 as I think it requires uprating to at least an 80amp RCD.

Now, if I get the go ahead to change the RCD, because I am altering the board slightly, am I required to bring it upto 17th edition (ie split the circuits up onto two RCD's or pop the circuits on RCBO's) or can I simply change the existing RCD for an 80amp type???

Thanks all
 
Not sure how you could justify a code 2 without confirming the size of the main fuse.

I agree but even more importantly, the installation has been in use for 10 years without any signs of damage and with diversity, that 63A rated device will be more than adequate. Code 4 for me.
 

Reply to RCD rating too low in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
300
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
812
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
869

Similar threads

As per above from Dave. Swap to a 63A outlet and problem goes away. What gets plugged into it is not part of an inspection.
Replies
20
Views
2K
  • Question
This contactor you suggested unfortunately only has two NO switches rather than 1 NC and 1 NO required for the CR3 current sensing bypass...
Replies
14
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top