RCD Requirement on 32 amp 3 phase socket in commercial kitchen | on ElectriciansForums
Discuss RCD Requirement on 32 amp 3 phase socket in commercial kitchen in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
T
timmy123
I am installing a 32 amp socket in a commercial kitchen (3 phase) to supply a 12 kilowatt oven. The cable is to be run from a remote DB through a ceiling void and down to the socket point in metal trunking (cable to be 5 core SY armour braided).
My question is whether RCD protection is theoretically required as the socket outlet exceeds 20 amps. The wording in regulation 411.3.3 seems open to interpretaion. Any input would be greatly appreciated.
Many Thanks
the socket is solely for the use of a piece of stationary equipment so doesnt need a rcd.
and will probably be a 5 pin commando socket anyway
Reply to RCD Requirement on 32 amp 3 phase socket in commercial kitchen in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
As per above from Dave. Swap to a 63A outlet and problem goes away. What gets plugged into it is not part of an inspection.
When I was on the electric board We had a pair of pillocks connect a housing estate to a very large genset, the n lead was in two parts and not...
4K