originally in the 16th. RCD protection for sockets likely to be used outdoors. 1991.
 
yes, indirect contact would be eliminated by the operation of the OCPD in the event of a fault.
 
later amendments to 16th stipulated RCD protection for sockets for general use. can't remember exactly when. mid to late 90's? then on the issue of 17th , RCDs were stipulated for the benefit of kitchen fitters, picture hangers, and general Destroy it Yourself merchants. ( cables buried in walls )
 
later amendments to 16th stipulated RCD protection for sockets for general use. can't remember exactly when. mid to late 90's? then on the issue of 17th , RCDs were stipulated for the benefit of kitchen fitters, picture hangers, and general Destroy it Yourself merchants. ( cables buried in walls )

Dont MCBs offer protection against picture hangers?
 
not if the nail just contacts with the L. if a cable is enclosed in earthed metallic conduit/sheath, that would trip a mcb.
 
Hopefully what ever is in contact with the nail can pass 30ma. If its just wood Id think no trip.
 
Hopefully what ever is in contact with the nail can pass 30ma. If its just wood Id think no trip.

You'd be right. But the moment a person touched the nail, then 30mA might pass through them and be very quickly turned off.

Without the RCD a few amps would have to flow (by which time they'd be dead).

Of course, nothing at all to stop that person thinking, "Huh!" and resetting the RCD again.
 
When were RCDs mandated in the regs? Im thinking mid to early 90s?
Early 80's (15th edition) This was for socket outlets that were specifically intended to supply equipment outdoors and I presume came about with the intention of reducing the number of fatalities when people were simply trimming their hedges and mowing their lawns.
 
Early 80's (15th edition) This was for socket outlets that were specifically intended to supply equipment outdoors and I presume came about with the intention of reducing the number of fatalities when people were simply trimming their hedges and mowing their lawns.

What was behind those fatalities? Damaged cords or missing CPC?
 
You'd be right. But the moment a person touched the nail, then 30mA might pass through them and be very quickly turned off.

Without the RCD a few amps would have to flow (by which time they'd be dead).

Of course, nothing at all to stop that person thinking, "Huh!" and resetting the RCD again.

You have a point here. Though I can still see current trickling into a wood stud turning it into charcoal.
 
It's funny, I have owned a house for 29 years but never had an RCD :)
My current house does have MCBs but sadly no RCD!
Perhaps I should upgrade my CU to a nice shiney metal one :)
 
It's funny, I have owned a house for 29 years but never had an RCD :)
My current house does have MCBs but sadly no RCD!
Perhaps I should upgrade my CU to a nice shiney metal one :)
and while you're at it, fabricate a non-combustible, i.e. ferrous metal cabinet for your chip pan. according to statistics, 50 x more house fires are caused by chip pans igniting than by plastic CUs.
 
later amendments to 16th stipulated RCD protection for sockets for general use.

I don't think that's right. I think it remained as socket outlets likely to be used to supply equipment outdoors.

I could easily check my blue copy of the 16th (the same as the brown one except it doesn't contain the harmonised colours change), but unfortunately I'm too lazy at the minute!
 
and while you're at it, fabricate a non-combustible, i.e. ferrous metal cabinet for your chip pan. according to statistics, 50 x more house fires are caused by chip pans igniting than by plastic CUs.

Think I will stay in bed, unless this is now deemed unsafe?
 
all depends if you smoke in bed. i once asked a bird if she smoked in bed. she said "don't know, I've never looked"
 
OK. Felt bad about being lazy.

16th Edition (BS 7671:2001)

471-16 Supplies for portable equipment outdoors

474-16-01
A socket-outlet rated at 32A or less which may reasonably be expected to supply portable equipment for use outdoors shall be provided with supplementary protection to reduce the risk associated with direct contact by means of a residual current device having the characteristics specified in Regulation 412-06-02(ii).

This regulation does not apply to a socket-outlet supplied by a circuit incorporating one or more of the protective measures specified in items (i) to (iii) below and complying with the Regulations indicated:

(i) protection by SELV (see Regulations 411-02 and 471-02)
(ii) protection by electrical separation (see Regulations 413-06 and 471-12)
(iii) protection by automatic disconnection and reduced low voltage systems (see Regulation 471-15).
 
OK. Felt bad about being lazy.

16th Edition (BS 7671:2001)

471-16 Supplies for portable equipment outdoors

474-16-01
A socket-outlet rated at 32A or less which may reasonably be expected to supply portable equipment for use outdoors shall be provided with supplementary protection to reduce the risk associated with direct contact by means of a residual current device having the characteristics specified in Regulation 412-06-02(ii).

This regulation does not apply to a socket-outlet supplied by a circuit incorporating one or more of the protective measures specified in items (i) to (iii) below and complying with the Regulations indicated:

(i) protection by SELV (see Regulations 411-02 and 471-02)
(ii) protection by electrical separation (see Regulations 413-06 and 471-12)
(iii) protection by automatic disconnection and reduced low voltage systems (see Regulation 471-15).

I gave you a 'like' for that
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
RCD requirments
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
25

Advert

Thread statistics

Created
Gardner,
Last reply from
Farmelectrics,
Replies
25
Views
3,131

Advert

Back
Top