J

JONOXNAM

Hi All, I was called to an RCD tripping problem tonight and I have found the cause which was a intermittent problem on a lighting rig.

My issue is that during my testing I did a slope test of the 100mA RCD protecting the main board. It was tripping at 65mA, my question is what value is acceptable for a 100mA RCD to trip at?


I have the 2391 & 2330 L3 but cannot remember any min times.

Thanks, Jon.
 
Great thanks.

One final Q I do all 3 phases but was told that this is not required as any phase shows the devices is working any comment?
 
I would aggree with that as all 3 phases go through the RCD with the neutral.

Make sure you test it on both sides of the sine wave and record the highest 1 X only.

The max trip times will depend on the RCD a BS only number will be 200ms and a BSEN 300 ms.

Have a look at this post
[h=3]3 Phase RCD testing[/h]
 
Last edited:

Reply to RCD slope test - any help on when an RCD is tripping too fast... in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
307
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
828
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
924

Similar threads

I don’t see an rcd here. Is it elsewhere, supplying this board? It looks like it’s in a garage… is there excessive moisture getting into...
Replies
7
Views
1K
  • Question
Assumption is the mother of all major foul-ups! Start with the basics, like IR testing, RCD testing on its own, and checking the leakage as...
Replies
7
Views
727

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top