B

bredon86

I am testing a site which has a ring main on a mcb but has an rcd socket. Do I need to put the rcd results on my cert?
 
Sorry, I should have said to make a note in the comments box stating that it is just for that socket outlet, or you could just add an extra row on the sheet for that socket, as the whole circuit is not RCD protected.

But yes, you test in the normal way, 1/2, X1, X5 at 0 and 180 degrees if it is a 30mA or less rcd used for additional protection.
 
You may need to list each one seperately, as each one needs to be tested and noted. you cannot add the value for the circuit unfortunately, as said the circuit itself is not RCD protected, just each outlet is.

It would help if they were individually named/numbered.

I forgot to add the functional test at the end too (the push button).

Are you using sampling ?, or is it a 100% test ?
 
You only need to test the circuit (RFC) once though for your (R1+R2), Zs, IR tests, and then note each outlet as belonging to that circuit, like I say it would help if each outlet was uniquely identifiable, ie. numbered or similar, the aim is to be as unambiguous as possible to what is and isn't tested.
 

Reply to Rcd sockets in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
315
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
841
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
954

Similar threads

As per above from Dave. Swap to a 63A outlet and problem goes away. What gets plugged into it is not part of an inspection.
Replies
20
Views
2K
That was rather lazy wording on my part. I wasn't testing those as part of the TEIC or completion certificate. These sockets had had appeared...
Replies
6
Views
533

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top