Hi all,
Any ideas on this one greatly appreciated.
Powerbreaker rcd spur supplying manrose LV extractor fan and ADS 28watt 2D Ip65 bulkhead in wetroom trips ocasionally for no apparent reason.
All wiring to wetroom is new, supplied from rcd spur and does not feed any other circuits in the house. The rcd spur is supplied from the house lighting circuit, 60898 B 6A mcb with no rcd protection at source. (obsolete senate consumer unit).
TNS system, R1R2 is 0.85 ohms, Zs is 1.47 ohms, insulation resistance is 150 mega ohms + on L, N and cpc and rcd tripping time is 50 and 25ms respectively.
Light fitting, rcd spur and timed extractor fan lv unit all changed for new but fault still exists.
Greatly appreciate any ideas to resolve the issue as have just about run out of ideas myself.
Thanks