Lack of earth.
Not on any RCD I can recall. Test button connects a resistor between one pole on the input side and one of the other poles on the output side, creating a 30mA or so difference (on a 30mA RCD) between whatever current is flowing through those two poles.
No earth connection involved.
 
Not on any RCD I can recall. Test button connects a resistor between one pole on the input side and one of the other poles on the output side, creating a 30mA or so difference (on a 30mA RCD) between whatever current is flowing through those two poles.
No earth connection involved.
you may well be correct but I have known some rcbo's to not trip when the flylead is disconnected.
 
Possibly an extra test built in to ensure that the earth lead is connected, but not since the days of the old voltage operated earth leakage detectors (yes, I am that old), has there been a requirement for a current to flow in the cpc for said breaker to operate. RCDs detect a difference in the sum of the currents flowing through its poles. The sum should be zero, but if exceeds 30mA, then off it should trip.
 

Reply to RCD test button in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
600
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
2K

Similar threads

  • Question
I would add though that a typical good TT rod of 100 ohms only needs 3V to have 30mA flowing and so trip an RCD, you might find that sort of N-E...
Replies
8
Views
722
  • Question
Yes I touched on diverted neutrals when I went over guidance note 3 the first time but I’m doing a second round and going between all books whilst...
Replies
9
Views
467

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top