just before i start this thread i would like to point out that rcd tests should be carried out at the load side of the rcd

got a call out to a fault where the a 30ma rcd kept blowing to the stage where it wouldn't reset, there were only 2 circuits involved one 6a lighting and one 16amp radial, all the wiring i did from new about a year ago

1st thing i did was turn the power off and swap the rcd for a new one, power on and the rcd never tripped.
did a full auto rcd test on load side of rcd with breakers off and the results were good

ok so i've got the power working again but haven't found the fault that originally blew the rcd,
out of curiosity i wondered if doing a full auto rcd test at each mcb would highlight any problems
tested the light circuit and the results were good
tested the radial circuit and at x1 my fluke tester gave a error 4 message which is a earth error

wasn't sure if i was on to anything here so i unplugged everything from the radial and insulation tested it, all fine,
then when everything was disconnected i also rcd tested from the mcb which gave a good results no error 4
then i decided to start plugging in appliances one by one to see if effected the rcd test
got to a fridge freezer and the error 4 came back,

still not totally convinced this appliance was faulty i decided to put the fridge freezer on a different rcd and wait to see if this rcd trips

hopefully find out if it was the fridge freezer on Tuesday

would be handy to know if this method of testing does pick up faults in the appliances ????

the best thing to do would be to pat test the appliance or attach a clamp meter to the cpc and record any earth leakage, but didnt have those tools on me
 
Chances are it`l be that fridge freezer as they are known to develop earth leakege problems with age. Do you know anyone who can pat it for you. If the rcd is staying in without that appliance connected then you may have found the problem however, it might be a combination of several appliances that just tipped it over the edge...........
 
Good question chris. Best to try and see: its a process of elimination. It seems to me that you have decided it was the fridge so i would go for that. Plug it in, get it warmed up then pat it......see what you get......
 
Hi chris, I'm not sure what your "test method" has told you because I think your interpretation may be based on a false premise. I leave that to you to decide in light of the following information.
Error Code 4 on a Fluke 165x series MFT actually indicates the test has been inhibited because the MFT has detected a Fault Voltage equal or greater than the preset level. Only two preset levels are able to be set, 25V or 50V, for nearly all installations, including domestic, it should be set to 50V. To check the setting look at the top right hand corner of the MFT display, it should read U[SUB]L[/SUB]=50V, if it reads U[SUB]L[/SUB]=25V press F4 to toggle the setting.
You like many others interpret Error Code 4 as an "Earth Fault" it's an easy mistake to make. If the green lead ("earth") has a poor connection (or is disconnected) the MFT thinks that the green lead is at some potential in excess of the preset Fault Voltage and therefore inhibits the test. Often remaking the green connection and retesting allows a reading to be obtained because now the MFT sees a normal safe voltage on the green lead. However, with a sound connection, if the test is still inhibited (Error Code 4) the MFT has detected a true excessive Fault Voltage. In this case you will need to check the installation, in particular, the voltage between N-E.
 
Last edited by a moderator:
Hi chris, I'm not sure what your "test method" has told you because I think your interpretation may be based on a false premise. I leave that to you to decide in light of the following information.
Error code 4 on a Fluke 165x series MFT actually indicates the test has been inhibited because the MFT has detected a fault voltage equal or greater than the preset level. Only two preset levels are able to be set, 25V or 50V, for nearly all installations, including domestic, it should be set to 50V. To check the setting look at the top right hand corner of the MFT display, it should read U[SUB]L[/SUB]=50V, if it reads U[SUB]L[/SUB]=25V press F4 to toggle the setting.
Touch voltage.......
 

Reply to rcd test picking up faulty appliance?? in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
354
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
905
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

I don’t see an rcd here. Is it elsewhere, supplying this board? It looks like it’s in a garage… is there excessive moisture getting into...
Replies
7
Views
1K
  • Question
I would add though that a typical good TT rod of 100 ohms only needs 3V to have 30mA flowing and so trip an RCD, you might find that sort of N-E...
Replies
8
Views
691

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top