sparko

When doing the rcd test on sockets. Do you repeat the test at every socket in the ring or just at the middle of the ring, and within what time does the rcd have to trip at x1 its tripping current 200ms or 300ms? Thanks
 
When doing the rcd test on sockets. Do you repeat the test at every socket in the ring or just at the middle of the ring, and within what time does the rcd have to trip at x1 its tripping current 200ms or 300ms? Thanks


doing the tests at roughly the middle socket is exceptable and the tripping times of rcds depends on the rating of that particular rcd ie 30mA IS 40ms
 
When doing the rcd test on sockets. Do you repeat the test at every socket in the ring or just at the middle of the ring, and within what time does the rcd have to trip at x1 its tripping current 200ms or 300ms? Thanks

If you do the tests at the DB, it can be a lot easier and faster.

For a BS61009/61008, the 1X maximum trip time is 300mS.

For the older BS4293, the 1X maximum trip time is 200mS.

Both should have a max of 40mS on 5X
 
When doing the rcd test on sockets. Do you repeat the test at every socket in the ring or just at the middle of the ring, /QUOTE]

You are testing the charecteristic of the Rcd,this should be done on the load side with all loads disconnected
As advised,it is best tested at the consumer unit
You dont have to Rcd test at the sockets themselves,anywhere on the ring
 
doing the tests at roughly the middle socket is exceptable and the tripping times of rcds depends on the rating of that particular rcd ie 30mA IS 40ms



It does'nt make any difference where in the circuit you do the test from, given the opperating speed of an RCD the closer to the rcd the easier it is to reset during the test cycle.
 
Yes but if the RCD is required work in real life the load will not be disconnected, so don't think that they are always going to react as your tester said they would.

I'm telling you the correct procedure for rcd testing as per IEE Guidance Note 3, not my opinion...
 
GN3 recommends to test between the the line conductor of the circuit and the cpc with the load disconnected.

This could be done at ANY socket and NOT the CU. You cannot have implemented safe isolation and test at the CU as the RCD test is a live test.
 
Last edited by a moderator:
GN3 recommends to test between the the line conductor of the circuit and the cpc with the load disconnected.

This could be done at ANY socket and NOT the CU. You cannot have implemented safe isolation and test at the CU as the RCD test is a live test.

As is Ze and PFC....
 
Both carried out with the Main Switch in the OFF position

But still a live test!

How will you test trip times on a lighting circuit fed via rcbo, up at a luminaire or at the consumer unit?

It's all about competence!
 

Reply to Rcd test in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
291
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
795
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
827

Similar threads

Seen this where T&E has been fixed with a flat bend of too tight a radius.
2 3
Replies
35
Views
1K
  • Question
Assumption is the mother of all major foul-ups! Start with the basics, like IR testing, RCD testing on its own, and checking the leakage as...
Replies
7
Views
725

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top