I

irishsailor

Hi

When testing from Isolator end can you please tell me the method for testing RCD, using a Megger 1553, can you use both 2 or 3 test lead method and can you explain both methods

Many Thanks

Chris
 
There shouldn't be any need for using 3 leads, as all you're doing is leaking 30mA to earth, so only line and earth clips needed.

So clip your green to the earth of the isolator, stick your red probe on your line, and press the autotest button.... Or do the 1/2 test, 1x (0 and 180), 5x (0 and 180) and once all these are done, press the test button one last time to make sure you haven't broken the RCD testing it.
 
Not as far as I am aware, as all that is needed to check that the RCD trips is to put that imbalance in the line and earth. I suppose you could use the 3 lead set, but I think you'd just be wasting time and energy as I don't think the Megger uses that connection for RCD tests.
 

Reply to RCD Testing Mini Shower CU in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
273
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
770
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
777

Similar threads

As per above from Dave. Swap to a 63A outlet and problem goes away. What gets plugged into it is not part of an inspection.
Replies
20
Views
2K
  • Question
Assumption is the mother of all major foul-ups! Start with the basics, like IR testing, RCD testing on its own, and checking the leakage as...
Replies
7
Views
724

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top