D

devon1

On some RCDs when I test at the board I can't get any Reading and the device will not trip, but if I do the same test at the socket it works. Why is that? I usually test at the distribution board the full test.
Thanks in advance
 
Poor or incorrect connection of the test leads is all I can think of.
There's no other reason why the test would complete correctly at a socket outlet but not at the board.

Are you using the "13A plug" test lead for socket outlets and then the standard test leads at the board?
Test them all for continuity, wiggling them to see if there is an intermittent connection on any of them!
Remember it could be on that third lead you don't use so often...

Simon.
 
Thanks, no it's not the test leads. All connections are good.

It happens with MEM RCDs. A lot of them, so far about 30 of them.

I have recently tested about 1100 Rcds at large department stores and funny enough someone told me that if an RCD fails at the board it can pass if you plug in at a socket and test. I didn't really understand how that could be so, but only one week later i have come across this same problem with the MEM rcds.

Non of the MEM rcds will pass at the DB , but will pass when plugging in at the socket. When i'm testing at the DB the RCD tester shows ALL green good connections , i push the button and no trip and time out.

in a couple of days i will check the MA and settings of the MEM rcds,
and keep you posted of any solutions.
thanks
 
Last edited by a moderator:
We have come across this a few times, and found that with some MEM rcd's and rcbo pods, the sensing circuit for the rcd is actually after the terminal where the wire is terminated ie. the coil is above the terminal screw. These devices will not trip if you test them by probing onto the terminal screw as the fault is introduced before the coil. As long as it passes the test at the socket, I would suggest there is no problem.
 
I have read in the professional electricians mag, there was a part from megger that went along the lines of:

The circuit is part of the coil and so when tested at the RCBO/RCD it will not trip as your not testing the complete coil.
I didn't understand this myself, and for the life of me I can't find that mag anywhere....

If I do find it I'll post it
 
We have come across this a few times, and found that with some MEM rcd's and rcbo pods, the sensing circuit for the rcd is actually after the terminal where the wire is terminated ie. the coil is above the terminal screw. These devices will not trip if you test them by probing onto the terminal screw as the fault is introduced before the coil. As long as it passes the test at the socket, I would suggest there is no problem.

Thanks for the post, i think your post is the answer.
The MEM rcds are quite big devices and there is 'a part' (which i imagine to be the coil) after the live terminal. Therefore to test at the terminal does not trip the device.
Great post by the way on only your third post, cheers!

edit added; I have tested other circuits with the coil separate and after the connection terminal ( the coil being a separate device about 20cm away. These devices did still trip at the connection point. Perhaps it's the type of MEM coil that causes it.
 
Last edited by a moderator:
I have read in the professional electricians mag, there was a part from megger that went along the lines of:

The circuit is part of the coil and so when tested at the RCBO/RCD it will not trip as your not testing the complete coil.
I didn't understand this myself, and for the life of me I can't find that mag anywhere....

If I do find it I'll post it

Thanks for info, Apesolutions answer would cover this.
Because the cable passes the coil after the termination at the RCD.
 
I have tested the MEM rcds at the DB.

Switch off the rcd. Disconnect the live cable, connect a test cable with a terminal block on the end ( secure safetly) . Test at the terminal block. reinstate. Continue testing all rcds at the DB.
 

Reply to Rcd testing, no trip at DB in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
291
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
800
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
830

Similar threads

If it’s rcbo’s, then it’s 30mA per circuit… an rcd mainswitch is 30mA for ALL circuits It may just be a cumulative earth leakage which was just...
Replies
9
Views
587
  • Question
It can also mean lasts or continues for two years.
Replies
14
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top