What do you have to test when your testing rcd?
Just record 1x and 5x? and for nonsence tripping at 0.5x (which it shouldn't trip)
And I have looked in regs, but can't seem to find a table for maximum reading? But I quickly looked in the OSG and it says should trip within 200ms for 1x and within 40ms for 5x ..... is this correct and all I need to test for with the RCD? Plus record on the forms what amp and mA rating it is..
Just record 1x and 5x? and for nonsence tripping at 0.5x (which it shouldn't trip)
And I have looked in regs, but can't seem to find a table for maximum reading? But I quickly looked in the OSG and it says should trip within 200ms for 1x and within 40ms for 5x ..... is this correct and all I need to test for with the RCD? Plus record on the forms what amp and mA rating it is..