Hi guys i have confused myslef completly now!!
RCD test
Reason: To make sure RCD's trip within the correct time
Method: An RCD tester is connected and a test at 1/2 times, 1 times and 5 times the trip current is performed on each side of the cycle and a time of trip obtained. Usually milli-seconds with the highest being recorded. The manual test button is then pressed.
Thats right??
But what do i record in my cert? is it really the highest?
Can someone explain why im testing at 1x and 5x please i thought 5x was for additional protection but i have really confused myself...
So at 5x the disconnect time needs to be under 40ms?
and at 1x needs to be 300ms or 200ms for older type.
Think im getting confused on the cert where it asks for maxium disconection time 4s?
Thanks for the help really love this forum!
RCD test
Reason: To make sure RCD's trip within the correct time
Method: An RCD tester is connected and a test at 1/2 times, 1 times and 5 times the trip current is performed on each side of the cycle and a time of trip obtained. Usually milli-seconds with the highest being recorded. The manual test button is then pressed.
Thats right??
But what do i record in my cert? is it really the highest?
Can someone explain why im testing at 1x and 5x please i thought 5x was for additional protection but i have really confused myself...
So at 5x the disconnect time needs to be under 40ms?
and at 1x needs to be 300ms or 200ms for older type.
Think im getting confused on the cert where it asks for maxium disconection time 4s?
Thanks for the help really love this forum!