Just a quick question I've got a dual rcd board with sockets on each rcd so it's easy to test, is there a best place to do the rcd testing, ie at the start of the ring, middle or end, I no your testing the same same rcd where ever you carry out the test but I didn't no if it made a difference,
Thanks chris.
GN3 says you test an rcd on the load side with the load disconnected. i would always take this as being at the terminals but its safer to use the plug adaptor and plug into the nearest socket
When officially recording the testing of these devices, you follow the manufacturers instructions (as well as GN3)!! NOT what happens to be easier!! What do you mean by safer?? the circuit conductors are disconnected from the device for testing??
Reply to Rcd testing in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
As per above from Dave. Swap to a 63A outlet and problem goes away. What gets plugged into it is not part of an inspection.
Assumption is the mother of all major foul-ups! Start with the basics, like IR testing, RCD testing on its own, and checking the leakage as...