hi, i am trying to find out how to test a RCD if it has a fault. i am using a fluke 1653b unit to test with. can some one help me in how to test the RCD, if it is to sensativ..i have fitted a comsumer unit in a house and the ring mains is tripping the RCD all the time but only when something is switched on in the kitchen ..
 
Do a ramp test, then an auto test (1xIn.....5xIn etc) but it sounds like a faulty appliance in the kitchen if it only trips when something is switched on. And as above, do the IR test, if you already havent.


Jay
 
Might have a problem testing it with the Fluke if he is using the Plug lead, as the ring keeps tripping it.

Just disconnect from the one side of the RCD and turn it on if it stays on then, select RCD test on the fluke but use the probes.


More than likely its not the RCD its an imbalance somewhere, get the rest of the dead tests done again fist and post the results.
 
if the RCD is faulty will it trip before the x5 or will it just give a high reading...the house is a mess because they had some fool doing an exstention and cableing up and i had to diconect it all because it faild.. the hole house is on one ring mains (kitchen, all rooms, three beroon house.....thank u for the information so far.
 
As others have said, disconnect all loads from the RCD, then carry out a ramp test and then the 7 tests described in GN3. Should all them results be fine then its time to test the fixed wiring.
 
hi, i am trying to find out how to test a RCD if it has a fault. i am using a fluke 1653b unit to test with. can some one help me in how to test the RCD, if it is to sensativ..i have fitted a comsumer unit in a house and the ring mains is tripping the RCD all the time but only when something is switched on in the kitchen ..

Appliance fault ? not the hard wire pull all plugs and switch off DP switches and try again sounds like you may be slightly out of your depth
 
hi, i am trying to find out how to test a RCD if it has a fault. i am using a fluke 1653b unit to test with. can some one help me in how to test the RCD, if it is to sensativ..i have fitted a comsumer unit in a house and the ring mains is tripping the RCD all the time but only when something is switched on in the kitchen ..
ramp it kid...
 

Reply to RCD testing in the Commercial Electrical Advice area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
388
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
970
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Did a fuseboard change yesterday from an old wylex board to dual rcd on a TT system with 14ohms ZE and finished pretty late. Went back this...
Replies
0
Views
500
L
  • Question
My Understanding is the 6 Months interval is IET Guidance and this wording is incorporated onto the label which is a requirement in 514.12.2 where...
Replies
9
Views
673

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top