installed a new dual rcd cu today and on completeing my tests I noticed the zs values were slightly above the max permitted by bs7671.
All my other readings, r1+r2s ect were fine and the ze was 0.2 off the top of my head.
took a zs reading off the load side of both rcds and both values came out around 1.03.
rcd funcional tests were fine and so too were the tripping times.
my question is, i'm i ok calculating the zs values and making a comment on my cert such as, "zs values calculated as rcd falsifying readings" ?
thanks guys