J

james king

this is confusing me.

now i know that the rcd times are ....

bsen 61008 and 9 should be less then 300ms
bs 4239 should be less than 200ms
rcd sokets at 200ms

but say i have tested a rcd at x1 180 degree = 35.2 and x5 at 180degree at = 12.6

if i remeber correctly is it

x1= max 50ms
x5 = max 40ms ?
 
thank u acat.

what i do is put down the highest reading i get so eg.....

x1 0' = 26.6
x1 180' = 35.2

x5 0' = 7.6
x5 180' = 12.6

so i would use 35.2 and 12.6 correct?
 
yes you record the highest one time value if the cert does not have space for 1x and 5x. If it has room for both record both
 

Reply to rcd times at x1 and times x5 in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
303
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
818
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
884

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top