vardymr2
-
Hi all,
Yesterday i was asked by a landload to put a rcd within a ground floor flat, The CU already have bs60898 mcb's but no Rcd protection. So i got a 2way sub board with 80amp 30ma rcd and wired it into the meter tails before the CU. io have tested the flat and only problem i found was a NtoE fault on lights. Well even if i disconnect that circuit completely and turn the power on everything stays up until i put load onto the circuit the rcd trips it does not matter which circuit it is it will trip.
Also within the flat it has a 2 way off peak board for two heaters. The neutral for this board is wired into the earth block on a tnc-s supply fuse and not into a neutral terminal within the meter its self.
Do you think it could be this neutral on the off peak meter or any other idea's?
Yesterday i was asked by a landload to put a rcd within a ground floor flat, The CU already have bs60898 mcb's but no Rcd protection. So i got a 2way sub board with 80amp 30ma rcd and wired it into the meter tails before the CU. io have tested the flat and only problem i found was a NtoE fault on lights. Well even if i disconnect that circuit completely and turn the power on everything stays up until i put load onto the circuit the rcd trips it does not matter which circuit it is it will trip.