P

pushrod

Was at a relative's house (big and old) and they said they sometimes flicked a particular light switch and it caused the CU to trip. Said i would take a quick look!

It turns out it was a split load board about 6 years old with one rcd. All the light circuits were on the non rcd side and when it was tripping it was taking out the rcd and leaving the lights on!:confused:. Taking out a 6 amp mcb on the non rcd side isolated the light and there was nothing loose at the light fitting or the switch. They said it used to happen very regularly but was less frequent recently. Needless to say we couldn't get it to happen when i was there. The switch in question was a smiths time guard, that comes on at night, but other than that it appeared perfectly normal. Didn't have time for any tests.

Must admit i was pretty much at a loss why a circuit on one side should be taking out the rcd on the other side! Am i missing something obvious? Anyone any suggestions? cheers :)
 
I think you might be wrong :( I think I might be wrong too :D
If there is a N-E fault on the RCD circuit, then the RCD will trip in normal use well before any extraneous (to this circuit) current is able to trip the RCD.

A good point Ringer.

But with N/E faults being 'load dependant', it could be a case of the straw that broke the camels back.

In other words, the normal circuits on the RCD side are running just under the 'trip limit', and the additional imbalance, from the lighting (or another circuit), cause the trip.

It might look like the lighting circuit is causing the trip, but it could just be an accumulation of loads.:)

Can anyone think of another reason why a circuit on one side of the board will trip the RCD on the other??
 
Last edited by a moderator:
Thanks for all the replies, i had a chance to pop round there for literally 15mins this morning and just had time to test the rcd and it looks like the "laurels" go to Nick in this case for suggesting a faulty rcd as i couldn't get it to give a sensible reading in about 3 goes, just kept saying "trip". Didn't even have time for a quick IR tests on N-E so still unsure if there is a fault there as well so some of the explanations as to why it was happening could well be right as well. Apologies though as i reckon i held back a vital clue which was the very uneven distribution of load. There was a total max mcb rating of more than 140A on the 63A rcd!
Yesterday I asked this on the RCD Diversity thread.
"Anyone know how quickly an rcd cooks if you exceed it's rated capacity. Have you got much leeway and for how long?
Also what is the most likely damage? does it just take out the trip and leave you thinking it is still ok or does it stop it conducting altogether?"

There were no replies but i reckon i now know the answer;)

It is a crabtree board and a search for an 80A crabtree rcd hasn't shown anything locally. Will other makes fit crabtree? (Don't want to fit another 63A one) Reckon the load should be more evenly distributed but am guessing there are probs borrowed neutrals on the 3 or 4 lighting circuits and that is why someone has previously stuck them all on the same side!!!



 
oh my i hate them things with a passion WYLEX 80A 30mA DP RCD these are in screwfix may get them cheaper from senate , but ill be honest with you think the fault on the RCD would be to a failure in the electrionc side rather than the contacts over loading

Not surprised, things are normally cheap for a reason :D

When i change it i'll probs try taking the old one apart and see if there are signs of overheating in there - be interesting to see if there is anything obvious.
 

Reply to RCD trip with a difference! in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
351
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
898
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Seen this where T&E has been fixed with a flat bend of too tight a radius.
2 3
Replies
35
Views
1K
In my opinion replacing the consumer unit and waiting to see which RCBO trips is not a good fault finding technique. If the lighting circuit...
Replies
8
Views
690
davesparks
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top