Mathew Acreman

Hi all,

My sister has recently moved into a new property and is having problems with the RCD tripping (Centre one in below photo) when certain kitchen appliances are running, commonly the washing machine and dishwasher. It can also trip if I unplug the dishwasher whilst the washing machine is running. Does anyone know what is likely to be causing this?

[ElectriciansForums.net] RCD Tripping Advice needed.

Many Thanks
Mat
 
could be earth leakage on either or both appliances. also could be some leakage on other parts of the installation and the appliances are taking the RCD above the trip threshold. a ramp test on the RCD is the 1st thing i'd go for, followed by checking for leakage with an earth leakage clamp meter.
 
i'd say 90% of RCD trippings is due to faulty appliances but before narrowing it down to that you need to get the RCD ramp tested to see what mA its tripping at, 20+ and the RCD should be fine in which case one of the appliances has high earth leakage.
 
Tripping when unplugging - could be a faulty socket?

Have you got a long extension lead, so you could plug the machines into another socket? This wouldn't necessarily be conclusive though.

Are you a sparky?
 
Last edited by a moderator:
Thanks for all of your advice guys. Much appreciated. Murdoch, No, I'm not a sparky but i have a very basic understanding through my job as a touring sound engineer. I deal with stage and concert electrics on a a daily basis but am far from being a sparky :) . Was just trying to find out if it could be something glaringly obvious before she pays for someone to come look at at.

Cheers
 
wouldn't cost much for a sparks to check it for you. (not more than £50 if it was me). finding an elusive fault could be a bit pricy though.
 

Reply to RCD Tripping Advice needed. in the Talk Electrician area at ElectriciansForums.net

Similar Threads

Which rcd is it? Is it one for everything, one for a few circuits?
Replies
5
Views
359
In my opinion replacing the consumer unit and waiting to see which RCBO trips is not a good fault finding technique. If the lighting circuit...
Replies
8
Views
449
davesparks
D
I don’t see an rcd here. Is it elsewhere, supplying this board? It looks like it’s in a garage… is there excessive moisture getting into...
Replies
7
Views
1K
  • Question
A kettle boiling fish - thats your fault right there... or is it a red herring? :)
Replies
4
Views
2K
T
  • Article
New plumbing & heating system advice Hello, I'm installing a new central heating & plumbing system and just wanted to run through my design...
Replies
0
Views
199
tommyh311
T

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks