AJT83

-
Joined
Apr 24, 2018
Messages
5
Reaction score
3
Location
Manchester
Hi,

Recently got called to a job, a problem with the RCD tripping. Went through the usual procedures of unplugging everything however I realised it wasn't just tripping on one circuit. It trips if you turn the shower on, plug something into the cooker switch and if you plug something into the ring main. Did a ramp test on the RCD and got 27ma. Didn't have time to IR test as the customer was going out. Was hoping somebody could point me in the right direction for when I go back. I presume it's a Neutral - Earth fault but I just don't understand why it trips on 3 different circuits? Even just trying to get a ZS at a socket or the cooker switch trips it (obviously on no trip).

Customer did say they had a leak not so long ago though but don't see why that would cause a fault like this. The RCD just wouldn't reset if that was the case?

Thanks in advance
 
"Didn't have time to IR test as customer was going out"!!!!!
Mate that's the first thing you should have done. Farting about ramp testing and unplugging things, waste of time. Leave everything plugged in and do a 250v test LN-E. Five minutes will establish whether a fault is present. Only when you know what you are dealing with can you make an informed decision on how to proceed, then its time to start farting about unplugging things.
Sorry but it always leaves me open mouthed the number of electricians who come on here about tripping RCD's and haven't carried out IR tests.
 
"Didn't have time to IR test as customer was going out"!!!!!
Mate that's the first thing you should have done. Farting about ramp testing and unplugging things, waste of time. Leave everything plugged in and do a 250v test LN-E. Five minutes will establish whether a fault is present. Only when you know what you are dealing with can you make an informed decision on how to proceed, then its time to start farting about unplugging things.
Sorry but it always leaves me open mouthed the number of electricians who come on here about tripping RCD's and haven't carried out IR tests.

...You're gonna upset lad's who charge by the hour,with advice like that...;)
 
Thanks lads. I was hoping somebody would tell me it wasn't a N-E fault though ;) the house is rank and really don't want to spend any length of time in their!
bloody defeatist. ( and it's there, not their).
 

Reply to RCD TRIPPING - ADVICE PLEASE in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
951
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Which rcd is it? Is it one for everything, one for a few circuits?
Replies
5
Views
498
Have you notified Building Control of these works?
2
Replies
19
Views
966

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top