H

hotspothannon

Hi all...advice needed.
I have just replaced a MCB on my girlfriends board...as it was faulty and tripping intermittently. Whilst doing that I decided to 'tidy' up the board as it's a bit of a mishmash with labels and such. Whilst labeling....I went through the whole house finding what MCB fed what, now I found a 16amp MCB labelled 'immersion heater'. This took my interest as I knew she had this ripped out when she brought the house 10 years ago. I finally found this one breaker fed one single socket in her kitchen. This breaker was on lighting side of the consumer unit ie 'no RCD' protection. Behind the said single socket there is a pair of twin n earth, one connected to the supply on the socket, one left in the back - which is dead. I can only assume someone broke into the immersion heater supply and made this single socket part of the radial circuit.
I decided to just move the MCB over to the RCD protected side of the bus bar.... And that was that...labeled it up...everything great. Great until she came to use it. Normally all she had plugged in it was a 'air freshener'.... And this was OK. However we seen since you plug anything else in then as soon as it's switched on - the RCD trips. This is with any appliance, except ones without an earth...ie air freshener, phone charger etc.
Now here's my question.....would it be OK just to put the MCB back to the 'non RCD protected' side....where it worked perfectly well for 10 years? I have tried to find the route of the cable but it is in the kitchen behind a tiled wall right next to the door frame. I can't even make out if the cable goes up or down. Downstairs she has solid wood flooring ( so that ain't coming up) ....upstairs I have had the carpet up where all the old immersion heater was, and all the old wiring, however the feed to the single socket is not there.
I'm thinking there is a N-E fault somewhere...but it's like where????
Any advice would be appreciated
 
When you have the line supplied via RCD but the neutral not, this will cause an unbalanced load on the RCD, so it will trip when a load draws current. Move the neutral over to the RCD neutral bar and problem should be solved!
 
When you have the line supplied via RCD but the neutral not, this will cause an unbalanced load on the RCD, so it will trip when a load draws current. Move the neutral over to the RCD neutral bar and problem should be solved!

What, like Tel suggested in post No.3?

Do keep up at the back! :6:
 
Last edited:

Reply to RCD tripping after moving MCB in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
373
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
939
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Seen this where T&E has been fixed with a flat bend of too tight a radius.
2 3
Replies
35
Views
1K
In my opinion replacing the consumer unit and waiting to see which RCBO trips is not a good fault finding technique. If the lighting circuit...
Replies
8
Views
693
davesparks
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top