Testing some new cabinets today which had in them a PDU with a 30mA rcd upfront as main switch. ( We build among other stuff, communications cabinets for highways, railways, etc). First one tested tripped on 1/2 fault current. Tried another cab, same thing. Did a ramp test, (tester is Kewtech kt64), tripped at indicated 18mA, though it felt like it was going at 15mA, but the tester indicated 18 before it stopped. ( I think they test too fast for accurate diagnostics?) I would expect a 30mA RCD to hold until about 21-24, from experience, and would have been disappointed with 18, but for 11 to fail at 1/2? One the one hand, I hope I've missed something ever so simple so that we can ship these cabs tomorrow, but I think I've covered everything. Any thoughts?
 
Did you test at the RCD with no appliances connected? If they are ramping at 18mA then your tester might need calibrating as at 1/2 times it should be outputting 15mA.
 
Tested with probes, ( there's something not right about the word "probes"!) at RCD load side, tried another tester, same make, 2 years younger, tried a different test supply circuit, tried swearing at it, a lot, ( that usually works). They're A type , in anticipation of a rectifier being fitted by the client, but that shouldn't affect the test. The way I see it is no matter what the circumstances of the test, whether it's a simulated situation or real, it shouldn't trip at 1/2, it should trip at x1 and x5. Trip times for x1 and x5 were the same if that's any use? Shouldn't be too bothered as I've had enough of running a workshop and am going back into the field ( got a job as a scarecrow!), but strangely I care what leaves the 'shop whilst I'm there.
 

Reply to RCD tripping at 1/2 test in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
947
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top