Testing some new cabinets today which had in them a PDU with a 30mA rcd upfront as main switch. ( We build among other stuff, communications cabinets for highways, railways, etc). First one tested tripped on 1/2 fault current. Tried another cab, same thing. Did a ramp test, (tester is Kewtech kt64), tripped at indicated 18mA, though it felt like it was going at 15mA, but the tester indicated 18 before it stopped. ( I think they test too fast for accurate diagnostics?) I would expect a 30mA RCD to hold until about 21-24, from experience, and would have been disappointed with 18, but for 11 to fail at 1/2? One the one hand, I hope I've missed something ever so simple so that we can ship these cabs tomorrow, but I think I've covered everything. Any thoughts?
 
Testing some new cabinets today which had in them a PDU with a 30mA rcd upfront as main switch. ( We build among other stuff, communications cabinets for highways, railways, etc). First one tested tripped on 1/2 fault current. Tried another cab, same thing. Did a ramp test, (tester is Kewtech kt64), tripped at indicated 18mA, though it felt like it was going at 15mA, but the tester indicated 18 before it stopped. ( I think they test too fast for accurate diagnostics?) I would expect a 30mA RCD to hold until about 21-24, from experience, and would have been disappointed with 18, but for 11 to fail at 1/2? One the one hand, I hope I've missed something ever so simple so that we can ship these cabs tomorrow, but I think I've covered everything. Any thoughts?
27-27.5 is typical for a healthy 30mA RCD

- - - Updated - - -

Is your tester set to 30mA?

A work colleague had his set to 10mA and was wondering why it didnt trip XD
your kidding....
 
If the isolation of all equipment shows a correct test reading , I would then assume that you if you have computer equipment involved there is leakage from each piece , I would then look at the idea of separating the equipment to RCBOs , Another point you would have to consider is what these cabinets are being connected to when on site, I have connected PDA cabinets in the past and usually on their own circuit Identified as having high earth leakage currents , and the necessary precautions applied..
 
Thanks Ray, these cabs are empty at the minute apart from an IEC distribution strip.This morning I tested one of the RCDs on the bench, same results, then tested an ABB one right next to it and it was fine. They're getting returned. Thanks to all for your input.
 
A quick update. We got a new batch in and still the same results when testing on Auto, BUT test at 1/2 only, not Auto, and it passes.Doesn't seem right to me that it fails during one procedure, but passes in another. I'm going to get in touch with Kewtech and see if they can shed any light.
 
Thanks again for all the above;hopefully tester definitely set up correctly, as I was showing the newbie how to set it up! RCD is a Schrack 40/2/003-A

I notice it says 003-A at the end of the description , I am thinking thats 3 Ma as 30Ma is .030 A , best to check with manufacturers description , could just be the part number,,

I tried looking up Scrack but theres not much info , as most of the sites are in Polish , I would stick with what you know to be O/K with the ABB you tried ,,
 
Last edited by a moderator:
Thanks again for all the above;hopefully tester definitely set up correctly, as I was showing the newbie how to set it up! RCD is a Schrack 40/2/003-A
just from Ray's post I notice that Eaton / Moeller supply RCDs with the same part number, could well be Schrack are rebadged Moeller ones, I know nothing about Schrack but might be worth checking and getting some Moeller ones instead.
View attachment Moeller_Datasheet_FI-40_2_003-A_279187.pdf
 

Reply to RCD tripping at 1/2 test in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
949
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top