Testing some new cabinets today which had in them a PDU with a 30mA rcd upfront as main switch. ( We build among other stuff, communications cabinets for highways, railways, etc). First one tested tripped on 1/2 fault current. Tried another cab, same thing. Did a ramp test, (tester is Kewtech kt64), tripped at indicated 18mA, though it felt like it was going at 15mA, but the tester indicated 18 before it stopped. ( I think they test too fast for accurate diagnostics?) I would expect a 30mA RCD to hold until about 21-24, from experience, and would have been disappointed with 18, but for 11 to fail at 1/2? One the one hand, I hope I've missed something ever so simple so that we can ship these cabs tomorrow, but I think I've covered everything. Any thoughts?