E

elementps

Hi all,

Wondering if anyone could throw a few suggestions my way.

Was testing a few circuits last week in preparation for additions (extension of house). All going fine until i tested the RCD that the customer currently has installed, it tripped on half current test?

I am planning to go back for some further investigation.
I tested at socket outlet, so my first idea is test direct at consumer unit, possibly dissconect the load??

The board is MK with MCB's but slightly older, the new MCB's will need a busbar conversion to fit. It's a split load with the RCD covering sockets, one think that threw me was the RCD is 4 module, is this just how they were made? All i can see from MK catalogue in 4 module, is 3 phase equipment???

Customer didnt really want to change board, but I think its heading that way as changin mcbs to rcbos, converting busbar, possibly replacing rcd is all adding up. May as well fit a new board.

Any ideas/advice on reasons for the RCD trip appreciated.
 
I'd would test again with all loads disconnected like you say, then see what you get.

All loads should be removed anyway, all mcbs from that RCD off. If it still trips then its probably faulty
 
If you tested at a socket you may have had loads plugged in that would affect the result, though normally that would just give you inaccurate times on the X5 test.

I would be going towards a either a dodgy RCD, or if you had loads plugged in that had Protective Conductor currents on them.

As you know a 1/2 test puts a 15mA fault on the RCD so if it dodgy then it could trip at this, so do a ramp test and see what it is tripping at.

If you left loads on it, that did have protective conductor currents, then the 15mA may have been enough to trip it. So test it at the CU.
 
Sorry forgot to mention, did a ramp test, at socket, 17mA.

So as planned I will first discon everything and test at board.

Now if this is still bad readings obviously faulty RCD, however what should be my next plan of attack if its not?
 

Reply to RCD tripping at half current in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
301
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
813
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
869

Similar threads

Seen this where T&E has been fixed with a flat bend of too tight a radius.
2 3
Replies
35
Views
1K
Which rcd is it? Is it one for everything, one for a few circuits?
Replies
5
Views
498

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top