Hi, hope someone can help on this one since it has me stuck.
A lady had a new kitchen put in 2 years ago with a new range master induction cooker. Everything was fine for a year. Then the rcd covering the cooker, 2 socket circuits and 4 lighting circuits started tripping every time she put the kettle on the induction center ring. She called out range master thinking it was a fault with the cooker and they said it is fine and to put it on an rcbo. This is where I got involved.
I have put the cooker circuit from the mains switch to a rcbo with the rcd covering the other 6 circuits.
the fault occurs intermittently, it can happen several times a day or not for 2 days.
when I was there it was fine so I thought it was fixed. A week later I got a call. The rcd covering the 6 circuits was tripping when the center induction ring was used on the kettle.
Now these circuits are totally separate, rcbo from mains switch doing cooker, rcd doing another 6 circuits. It's a 17th edition board and the 2nd rcd is totally unaffected.
There was an extension lead behind the tumble dryer with a bad l-e ins res reading. This got removed off one of the socket circuits. The rcd tripped again today.
I have ins res tested between cooker cable and rcd busbar / neutral bar and >100mohms and live to earth ok. Have checked the rcbo and the operates fine 21/18ms and rcd 121/24ms. ramp test 22.5ma on rcbo
Have you any ideas why when the center induction hob is turned on it trips the rcd not the cooker circuit rcbo? It occurs when the cooker knob is actioned on intermittently, but only occurs with the cooker operation.
A lady had a new kitchen put in 2 years ago with a new range master induction cooker. Everything was fine for a year. Then the rcd covering the cooker, 2 socket circuits and 4 lighting circuits started tripping every time she put the kettle on the induction center ring. She called out range master thinking it was a fault with the cooker and they said it is fine and to put it on an rcbo. This is where I got involved.
I have put the cooker circuit from the mains switch to a rcbo with the rcd covering the other 6 circuits.
the fault occurs intermittently, it can happen several times a day or not for 2 days.
when I was there it was fine so I thought it was fixed. A week later I got a call. The rcd covering the 6 circuits was tripping when the center induction ring was used on the kettle.
Now these circuits are totally separate, rcbo from mains switch doing cooker, rcd doing another 6 circuits. It's a 17th edition board and the 2nd rcd is totally unaffected.
There was an extension lead behind the tumble dryer with a bad l-e ins res reading. This got removed off one of the socket circuits. The rcd tripped again today.
I have ins res tested between cooker cable and rcd busbar / neutral bar and >100mohms and live to earth ok. Have checked the rcbo and the operates fine 21/18ms and rcd 121/24ms. ramp test 22.5ma on rcbo
Have you any ideas why when the center induction hob is turned on it trips the rcd not the cooker circuit rcbo? It occurs when the cooker knob is actioned on intermittently, but only occurs with the cooker operation.