here's one to be aware of
today i installed some lights, fan and mirror light in a brand new bathroom, all new cable etc, tested R1+ R2 and insulation resistance all good, the feed came from existing light circuit and went into my rcd, (power breaker unit)
so went to liven it all up and the rcd tripped straight away, so thought maybe i got a switch and feed mixed up after testing, belled all switch's out and they were fine, pulled all the lights down to make sure polarity was correct which it was
really couldn't work out why the rcd wouldn't work, then i decided to do a zs test from the supply side of the rcd which pointed out their was no earth, had a look at some of the existing lighting circuit joint box's and the cpc's had just been chopped off and left unconnected..
ended up running a fly lead back to a joint box which did have a decent earth and this corrected the fault. took a couple of hours to rectify this problem and from now on i will always check zs before extending a circuit rather then later ,
i think the problem was down to induced voltage (eddy current) on cpc's which were not correctly earthed causing the rcd to trip???
the earthing system was tns
today i installed some lights, fan and mirror light in a brand new bathroom, all new cable etc, tested R1+ R2 and insulation resistance all good, the feed came from existing light circuit and went into my rcd, (power breaker unit)
so went to liven it all up and the rcd tripped straight away, so thought maybe i got a switch and feed mixed up after testing, belled all switch's out and they were fine, pulled all the lights down to make sure polarity was correct which it was
really couldn't work out why the rcd wouldn't work, then i decided to do a zs test from the supply side of the rcd which pointed out their was no earth, had a look at some of the existing lighting circuit joint box's and the cpc's had just been chopped off and left unconnected..
ended up running a fly lead back to a joint box which did have a decent earth and this corrected the fault. took a couple of hours to rectify this problem and from now on i will always check zs before extending a circuit rather then later ,
i think the problem was down to induced voltage (eddy current) on cpc's which were not correctly earthed causing the rcd to trip???
the earthing system was tns