Hi there.
I have been investigating a job where I am struggling to find any thing wrong with the wiring/installation.
It is a dual CGD split board with the non rcd circuits on top and the rcd protected circuits below.
The constant problem is that when the lights are switched on at the switch, it sometimes takes out the rcd, and also sometimes happens when other lights are switched on.
I have tesed all three lighting circuits and all three socket circuits and all seems fine.
I have checked the klick ceiling roses and light fittings for loose connections.
I have also carried out earth loop tests, rcd test and continuity on the 3 ring mains.
All the readings are fine.
The rcd test also prove that the rcd unit is working correctly and the tripping times are good.
My theory is that when the light fittings are being switched on, the start up current is affecting the rcd as the are 600x 600 modular flourescent fittings throughout.
Any advice would be good. Many thanks
I have been investigating a job where I am struggling to find any thing wrong with the wiring/installation.
It is a dual CGD split board with the non rcd circuits on top and the rcd protected circuits below.
The constant problem is that when the lights are switched on at the switch, it sometimes takes out the rcd, and also sometimes happens when other lights are switched on.
I have tesed all three lighting circuits and all three socket circuits and all seems fine.
I have checked the klick ceiling roses and light fittings for loose connections.
I have also carried out earth loop tests, rcd test and continuity on the 3 ring mains.
All the readings are fine.
The rcd test also prove that the rcd unit is working correctly and the tripping times are good.
My theory is that when the light fittings are being switched on, the start up current is affecting the rcd as the are 600x 600 modular flourescent fittings throughout.
Any advice would be good. Many thanks