Called out to fault on RCD tripping maybe twice in a month for sometime.
Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which made matters worst.
So refitted original RCD Type AC for the time being.
Insulation Resistance measurements were 20 M ohms.
Ring continuity fine too.
Testing proved difficult because of RCD tripping even with my Socket Tester, then everything went back to normal, power back on & days later still on.
Obviously Client not happy & believe’s ive done something.
The DB is a Stack DB,Crabtree Starbreaker all cabling brand new.
Its Split between Top & Bottom Main Switch mcb’s
Bottom RCD 30ma 80amp supplying 5 Ring Mains & 3 other Radial circuits MCB’s
i think I narrowered it down to-the kitchen/dining RM & UNPLUGGED all equipment but doing this the RCD still tripped.
Fingers crossed no call outs over Xmas… returning after hols … Any ideas fellow Sparkies😎
 
How did you ascertain that the original rcd was faulty? Did you test the original rcd with outgoing circuits disconnected? If you havnt got an earth leakage clamp meter you can connect one circuit back at a time and use ramp test on your mft with no circuits connected, note the ma, then add back one at a time to see when its requiring less ma to trip, could point you in the right direction
 

Reply to RCD Tripping intermittently in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
291
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
800
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
828

Similar threads

Seen this where T&E has been fixed with a flat bend of too tight a radius.
2 3
Replies
35
Views
1K
  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
947

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top