First time poster go easy on me.

Got a call out to a job today, got told the RCD was tripping. Even when no appliances plugged in. And so it was intermittently about every 20 mins. Only two ring circuits on the RCD, on one of the rings im getting continuity across line and netural on both legs. Its not taking the MCB out, no fault across the earth.

Tested the RCD for nuisance tripping all passed fine.

Cant get my head around why with a permanent short the MCB wont trip? Going back tomorrow morning for further investigation and feeling as if i should suggest re wire of sockets due to reasonably low IR readings anyway.

Any thoughts would be appreciated.
Cheers
 
I only ever read the post buzz, never the comments lol. For all I know I could constantly be repeating what others say.....


Appliance still plugged in. Cooker hood, FCU will be behind chimney.
Even turned off at socket, can still get an N-E fault to trip rcd.
Have you checked the mcb isn’t at fault?

Buy yourself a notepad and a pencil. For taking notes.
 
Is the heating fed by one of these circuits? If the RCD trips yet you've got good IR readings that implies an intermittent fault which can be caused by e.g. the heating/water heating coming on and there's a faulty component (pump, valve, boiler pcb, immersion element), or a compressor motor kicking in.

A healthy ring circuit has a natural earth leakage of about 3mA, the power supplies for modern equipment such as TVs, PCs, phone chargers etc also have quite high earth leakage; when it trips it could it be the sum of these exceeding 30mA.

Does it trip when you're there and have disconnected everything, or when stuffs plugged in/switched on?

Is there e.g. a PIR external light fed via a FCU on the circuit?
 

Reply to RCD tripping issue on ring circuit in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
388
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
970
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Seen this where T&E has been fixed with a flat bend of too tight a radius.
2 3
Replies
35
Views
1K
My guess is an earth to N fault in the damaged light fitting. This will become a problem when other devices draw large currents.
Replies
2
Views
352

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top