Can someone shed some light on a problem I'm having.
I changed a CU today as there were only 6 circuits they are all now rcbo's there was no rcd protection prior to that.
On the ground floor circuit the rcd test was x1@ 147ms and x5@ 23ms.
However now when the customer turns the heating on its fine and if they turn the hot water on at the same time it's tripping the rcd.
It is run from a fused connection unit and upon looking all looks good in the fcu.
It's a valiant ecotecplus 618 and the controller is a lifestyle lp522
I'm not a heating engineer but I may be missing something obvious.
 
Can someone shed some light on a problem I'm having.
I changed a CU today as there were only 6 circuits they are all now rcbo's there was no rcd protection prior to that.
On the ground floor circuit the rcd test was x1@ 147ms and x5@ 23ms.
However now when the customer turns the heating on its fine and if they turn the hot water on at the same time it's tripping the rcd.
It is run from a fused connection unit and upon looking all looks good in the fcu.
It's a valiant ecotecplus 618 and the controller is a lifestyle lp522
I'm not a heating engineer but I may be missing something obvious.
Any test results prior to swapping the CU
 
I think you have sort of answered your own question here.

1. I'm assuming you did the IR tests on the circuit from the CU to the boiler FCU

2. The heating is switched on and works

3. When the boiler "calls" for water, the RCBO trips.....
 
Logically if it trips when the hot water is turned on its in the boiler. I do know they have a motorised screw valve that is prone to leakage they may have this valve leaking. It operates when you call for hot water. When did they have their boiler service last. Its such a small leak that you may not see it outside the boiler.
 
I think you have sort of answered your own question here.

1. I'm assuming you did the IR tests on the circuit from the CU to the boiler FCU

2. The heating is switched on and works

3. When the boiler "calls" for water, the RCBO trips.....

Well i did not dosconnect the boiler or switch the fcu off so tested it all.

Yes the heating works but if you call for water at the same time it trips. However what seems strange is the heating works now when you call for water on and the heating button does the tripping. Im wondering of the controller is knackered.
 
Logically if it trips when the hot water is turned on its in the boiler. I do know they have a motorised screw valve that is prone to leakage they may have this valve leaking. It operates when you call for hot water. When did they have their boiler service last. Its such a small leak that you may not see it outside the boiler.
Yesterday they had serviced and we rang him. His answer was "it was working yesterday" obviously as there was no rcd prior to today then it would have worked and the CB would not trip.
 
Have you tried easing the controller and associated wiring behind it, to see if the fault replcates itself? Is there a room stat, cylinder stat & associate wiring?
Yes all of that. I did remove the controller but did not prod around inside.
When you turn the room stat off the boiler did not shut down we had to turn the controller off.
 
Well i did not disconnect the boiler or switch the fcu off so tested it all.

So if you didn't disconnect the "load" and you stuck 500v into the boiler, you may have damaged the boiler circuitry.

Tip: ALWAYS disconnect loads before doing IR tests AND not you think you have a fault, you MUST disconnect the boiler from the FCU and test the circuit PROPERLY so that you can eliminate this from your investigation.

What exactly were your IR tests? and how/where did you do your Zs tests?
 
So if you didn't disconnect the "load" and you stuck 500v into the boiler, you may have damaged the boiler circuitry.

Tip: ALWAYS disconnect loads before doing IR tests AND not you think you have a fault, you MUST disconnect the boiler from the FCU and test the circuit PROPERLY so that you can eliminate this from your investigation.

What exactly were your IR tests? and how/where did you do your Zs tests?
Zs at db was 0.35 ir was done at 250v however i took out the earth and neutral fly lead from the earth and neutral bar. And tested then i may have been doing it wrong. Its a wylex rcbo.
 

Reply to Rcd tripping issue. in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
301
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
814
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
873

Similar threads

Which rcd is it? Is it one for everything, one for a few circuits?
Replies
5
Views
498
  • Question
Hi Gingerrubix, The fact that your previous Tenant replaced a faulty socket plate which he used for an external EV, raises an eyebrow. Also your...
2
Replies
25
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top