e5c3d4
DIY
An RCD keeps tripping.
Please see attached photo of the board (2 photos attached). I’ll call the breakers:
MCB (1) marked ‘Upstairs lighting’
MCB (2) marked ‘Sockets’
MCB (3) marked ‘Water heater’
MCB (4) marked ‘Sockets’
RCD (5) for MCBs (1-4)
MCB (6) marked ‘Kitchen sockets’
MCB (7) marked ‘Downstairs lighting’
MCB (8) marked ‘Garage’
MCB (9) marked ‘Cooker’
RCD (10) for MCBs (6-9)
No appliances are plugged in to any sockets and all sockets are turned off.
Turning on MCB (4) trips RCD (5) every time.
It is possible to have all MCBs other than (4) on and not trip RCD (5). However, it will trip eventually, around every 30 mins.
Even with all of MCBs (1-4) off, RCD (5) occasionally trips.
Kitchen sockets are on a different circuit MCB (6) and RCD (10). Using high powered appliances in the kitchen (e.g. kettle) will also trip RCD (5). However, the appliance, MCBs (6-9) and RCD (10) all stay on.
RCD (5) is not faulty: it has been replaced.
I can’t use a socket tester other than in the kitchen as as turning on MCB (4) will trip RCD (5).
Any ideas much appreciated.
Tom
Please see attached photo of the board (2 photos attached). I’ll call the breakers:
MCB (1) marked ‘Upstairs lighting’
MCB (2) marked ‘Sockets’
MCB (3) marked ‘Water heater’
MCB (4) marked ‘Sockets’
RCD (5) for MCBs (1-4)
MCB (6) marked ‘Kitchen sockets’
MCB (7) marked ‘Downstairs lighting’
MCB (8) marked ‘Garage’
MCB (9) marked ‘Cooker’
RCD (10) for MCBs (6-9)
No appliances are plugged in to any sockets and all sockets are turned off.
Turning on MCB (4) trips RCD (5) every time.
It is possible to have all MCBs other than (4) on and not trip RCD (5). However, it will trip eventually, around every 30 mins.
Even with all of MCBs (1-4) off, RCD (5) occasionally trips.
Kitchen sockets are on a different circuit MCB (6) and RCD (10). Using high powered appliances in the kitchen (e.g. kettle) will also trip RCD (5). However, the appliance, MCBs (6-9) and RCD (10) all stay on.
RCD (5) is not faulty: it has been replaced.
I can’t use a socket tester other than in the kitchen as as turning on MCB (4) will trip RCD (5).
Any ideas much appreciated.
Tom