byron24

Hi all got a problem at a house where i changed the fuseboard the other day.

Replaced a wylex rewirable with a crabtree dual rcd board.

Both lighting on same rcd as sharing a common on the 2 way switching between upstairs and down.

Started to turn lights on and rcd tripped. Tried various rooms and turning lights on in different orders and rcd trips instantly sometimes and then after a few minutes other times.

Did insulation resistance tests between the earth bar and the line conductor for each lighting circuit and reading a dead short 0.00Mohms.

Did a continuity test between line conductors and earth bar and went round siwtching on different rooms. Some read open circuit and some came back with a reading of 40 - 100 ohms.

Cant see that there is a dead short on every other room as was all working before board swap.

Put them on the non rcd side and breakers stayed on.

Any ideas what might be causing this?
 
I had simular problem ,and agree with message nuetral fault .mine was the 2way lighting had borrowed nuetral which caused an unbalance .
 
Agree with others, I always totaly isolate circuits before testing especialy with pme. Its the only way to get accurate readings. Look for continuity between the nuetrals when everything is disconnected. You should get open circuit readings unless they are shared. Make sure lamps are in and try light switches both ways. Stick to 240v on your tests, in this instance. Also its prudent even essential to do a periodic before a board change it shows possible problems in advance.
 
Last edited by a moderator:
Hi I agree I now always test circuits before any board change or rcd install.Any n - earth fault will trip rcd not mcb - and you need to inform customers of the faults
 

Reply to Rcd tripping on board change in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
410
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
916
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
878

Similar threads

Exactly. I was going to ask on the earthing once he clears this boiler fault (suspect on internal component). OP mentions oil boiler but makes no...
2
Replies
19
Views
924
  • Question
Yes I touched on diverted neutrals when I went over guidance note 3 the first time but I’m doing a second round and going between all books whilst...
Replies
9
Views
603

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top