Been called into a job,electrician who started to find the fault,left & said he couldn’t find the fault,leaving the client running extension leads everywhere for lights,even in the bathroom.
Basically for what ever reason the rcbo trips ,it can be reset but trips again.
It’s a bungalow with joint boxes for the lights,& loads of fibreglass.Ive split the circuit so now half of the lights are on,but kitchen & diner are off.
The M ohm resistance of the faulty cable is L - E,N - E 0.09,L- N 6.90,
No idea why this cable is at fault,managed to get to all lights,they seem ok,not ideally terminated but looks ok.
Later today will try & get to switches & megger as I go along,the baffling thing,is that this fault is happening ,it a nightmare.
 
You've done well so far, keep gong in a methodical way.

Are there any outside lights?
I had exactly this once. I was called out to a house where the RCD kept tripping from the lighting circuit. After a couple of hours testing and searching the home owner decided to mention an old outside light that had "never" worked. The kids had been playing football a while back and had smashed the glass cover. But as the light never worked they just ignored it as it was down the side of an alleyway that they never used. Turned out the supply to the light was still intact and live, a water filled lamp holder was the problem.
 
try dissing the working part of the circuit. then try feeding the part that is currently dissed.if it works then it may be the MBC part of the RCBO that's tripping on inrush.
 
How many lights on the rcbo are they LV or 240v, do the lights trip on switching or randomly? any signs of rodent damage? have you or the other electrician changed the rcbo? If not what are the RCD test readings? Have you tested Live and Neutral joined together to earth on the insulation test?
 
If there are only 2 rooms to go .......... disconnect the lights at the switches .......... than add 1 by 1 to see how the IR results change, and if the light buld can be removed you NEED to do this. L&N to cpc isn't a great help in such situations.
 
How many lights on the rcbo are they LV or 240v, do the lights trip on switching or randomly? any signs of rodent damage? have you or the other electrician changed the rcbo? If not what are the RCD test readings? Have you tested Live and Neutral joined together to earth on the insulation test?
240Volts is LV
 
How many lights on the rcbo are they LV or 240v, do the lights trip on switching or randomly? any signs of rodent damage? have you or the other electrician changed the rcbo? If not what are the RCD test readings? Have you tested Live and Neutral joined together to earth on the insulation test?
Rcbo tests fine,they are 230 halogen lights,same results L+N to Earth 0.09.
 
I had exactly this once. I was called out to a house where the RCD kept tripping from the lighting circuit. After a couple of hours testing and searching the home owner decided to mention an old outside light that had "never" worked. The kids had been playing football a while back and had smashed the glass cover. But as the light never worked they just ignored it as it was down the side of an alleyway that they never used. Turned out the supply to the light was still intact and live, a water filled lamp holder was the problem.
Thanks,no luck there,ex lights are ok.
 

Reply to Rcd tripping on downlights in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
373
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
939
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Thank you for taking the time to help explain this - much appreciated
Replies
7
Views
866
  • Question
I would add though that a typical good TT rod of 100 ohms only needs 3V to have 30mA flowing and so trip an RCD, you might find that sort of N-E...
Replies
8
Views
693

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top