Been called into a job,electrician who started to find the fault,left & said he couldn’t find the fault,leaving the client running extension leads everywhere for lights,even in the bathroom.
Basically for what ever reason the rcbo trips ,it can be reset but trips again.
It’s a bungalow with joint boxes for the lights,& loads of fibreglass.Ive split the circuit so now half of the lights are on,but kitchen & diner are off.
The M ohm resistance of the faulty cable is L - E,N - E 0.09,L- N 6.90,
No idea why this cable is at fault,managed to get to all lights,they seem ok,not ideally terminated but looks ok.
Later today will try & get to switches & megger as I go along,the baffling thing,is that this fault is happening ,it a nightmare.
 
Lightweight:D

I am qualified level 3 with NICEIC

Trouble is people need to understand that RCD trips under an imbalance in the circuit for example some touching a live conductor.

But MCB'S trip under short circuit or overload

I guess the water conductivity acts as a bridge between the live and either neutral and earth.

Too many sparkies jump straight to testing rather than inspection first and even isolating the problem by visualising.

Yes I am a lightweight one bottle of wine and I'm knackered lol. Have a good boxing day
 
I am qualified level 3 with NICEIC

Trouble is people need to understand that RCD trips under an imbalance in the circuit for example some touching a live conductor.

But MCB'S trip under short circuit or overload

I guess the water conductivity acts as a bridge between the live and either neutral and earth.

Too many sparkies jump straight to testing rather than inspection first and even isolating the problem by visualising.

Yes I am a lightweight one bottle of wine and I'm knackered lol. Have a good boxing day
You to
 

Reply to Rcd tripping on downlights in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
376
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
944
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Thank you for taking the time to help explain this - much appreciated
Replies
7
Views
866
  • Question
I would add though that a typical good TT rod of 100 ohms only needs 3V to have 30mA flowing and so trip an RCD, you might find that sort of N-E...
Replies
8
Views
693

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top