Hi folks,

changed a CU over yesterday to a dual RCD board. Standard affair, all tests fine. Did live tests, started doing the Zs for the lights. Both up and downstairs lights kept tripping the RCDs. I'm using my Megger with the 3 leads to avoid tripping. Megger was set to No Trip Loop and all that. Zs for all other circuits fine

Am i missing something? .......cpc's are all present and correct in all circuits as i thought initially i may not be getting a good earth.

Stumped
 
are the 2 lighting circuits on the same RCD, or 1` on each? is there the possibility of there being some leakage existing, so that the Zs test current takes it over the threshold? do a ramp test on the RCDs.
 
are the 2 lighting circuits on the same RCD, or 1` on each? is there the possibility of there being some leakage existing, so that the Zs test current takes it over the threshold? do a ramp test on the RCDs.

lighting circuits are on different RCD's ....good idea re ramp test
 
Did you try testing the RCD's to establish if they are goosed or not???

Unlikely but needs ruling out at least.

yeah, good point but as all other circuits tested fine i ruled this out, bit hasty perhaps....

i'll go back and approach with a fault finding head on ....

thanks all!!
 

Reply to RCD tripping on "No Trip" Zs test in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
305
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
825
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
912

Similar threads

My guess is an earth to N fault in the damaged light fitting. This will become a problem when other devices draw large currents.
Replies
2
Views
344
Which rcd is it? Is it one for everything, one for a few circuits?
Replies
5
Views
498

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top