Hi, while testing the new board I installed I got to the live testing at the sockets one of the RCD's kept tripping during the loop test, the other ring tested fine so it's not the tester, the insulation tests where all good. Unfortunately I didn't have a residual current clamp meter with me, to see what was present in the existing circuits.
 
Does RCD test work at the RCD? Also check with outgoing Neutral disconnected if it's a dual RCD board.
Try a ramp test of the RCD and re-check dead IR tests.
The ramp test will tell you how many milli-amps of leakage it takes on top of what's already leaking to trip it.
And trying unplugging everything and doing it again, might simply be a faulty appliance.
 
Last edited:
Does RCD test work at the RCD? Also check with outgoing Neutral disconnected if it's a dual RCD board.
Try a ramp test of the RCD and re-check dead IR tests.
The ramp test will tell you how many milli-amps of leakage it takes on top of what's already leaking to trip it.
Many thanks for a very speedy reply, I did recheck all the IR tests. I will take your advice and try the above, unfortunately it won’t be for a few weeks but I will let you know .. cheers 👍
 

Reply to RCD tripping on test in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
265
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
756
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
740

Similar threads

L
  • Question
My Understanding is the 6 Months interval is IET Guidance and this wording is incorporated onto the label which is a requirement in 514.12.2 where...
Replies
9
Views
641
Seen this where T&E has been fixed with a flat bend of too tight a radius.
2 3
Replies
35
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top