This was an interesting problem and solution
I recently wired an community hall - the supply was a TPNE – one phase was being used for E7 heating. One phase was unused. And the third was to supply the lighting and power. I fitted a split board 12 way CU and ran two A2 radials for the sockets. The hall was fitted with around 30 wall mounted fluorescent lighting fittings via an 8 gang switchplate. I very wisely fitted a “lighting control” connection box (where all lighting cables terminated before going to the relevant switches and fittings) All circuits tested ok. But the RCD would trip occasionally when a light switch operated . The RCD would not always trip with the same switch . It could be any of the 8 – retested circuit – all ok, changed RCD – problem persisted . I took the lighting circuit off RCD protection (split board) . But the problem persisted. Fitted a separate CU for lights only with no RCD protection . Problem not solved. The RCD would still trip when light switches used (not every time , but now and again) I decided to put the lighting CU on its own phase – so utilised the unused phase. The problem still persisted. I eventually realised what the problem was ( Back emf on the neutral caused by inductive discharge lighting) . I solved the problem by fitted double pole light switches and switching both line and neutral conductors. First time in 40 yrs that I have come across this problem
 
that's sound good ,
but how did you get all the neutral down to the switches(grid)

I had taken all the cables to the fittings and from the switches to a large connection box- so it was an easy job to take neutrals down to switches ( I only had to change over a few connections inside the box) - but had to change the 8 gang to a 4 gang switch plate
 
Interesting! Must have been frustrating too..could have stumped many a good man

How many circuits controlled the lights? Did you realise it was the fittings by changing all
the lights on one circuit or was it a guess/measurement/deduction by elimination?

If you kept switching a switch on off on off on off would it definitely go at some point?

what fittings were they?

Well done!
 
Have to admit I would have struggled with that one well done for thinking it through.

Begs the question? What if the TPNE was feeding two flats and a Hall all on different phases? Same fault tripping the RCD in the imaginary flat?
Ps what was the earthing type?
 
Begs the question? What if the TPNE was feeding two flats and a Hall all on different phases? Same fault tripping the RCD in the imaginary flat? So true . I have used a similar scenario when trying to explain this problem to some of my students- It is like a light switch in one house tripping a neighbors RCD on the next street hahaha-
 
Ok well done but what made you think and how did you work out or find it was back emf I've always been very suspicious of this back feed on the neutral still struggle sometimes to work it out can anyone explain to me in idiot form lol

I arrived at the solution via inference and deduction . The neutral (and earth) were the only common factors. I know that inductors can cause back emf (Back EMF arises whenever current is removed from an inductive load). The inductive load resists the sudden change in current and produces a reverse voltage ) So I assumed that the back EMF was using the neutral and upsetting the local RCD.
 
Interesting! Must have been frustrating too..could have stumped many a good man

How many circuits controlled the lights? Did you realise it was the fittings by changing all
the lights on one circuit or was it a guess/measurement/deduction by elimination?

If you kept switching a switch on off on off on off would it definitely go at some point?

what fittings were they?

Well done!

I cant recall the fitting types (wall mounted, fluorescents) There were about 30 fittings controlled via 8 switches ( All terminations from fittings and switches went to a large connection box, which was fed from a single circuit from the Consumer Unit on a 10A MCB (if I recall correct ) Yes it was a guess/measurement/deduction by elimination after cyhanging all the switches and changing the RCD and fitting a separate CU etc. If I kept switching off a switch one of them would eventually trip the RCD. (usually after about 3 switches) As I said above. first time I have ever had this problem.
 
Last edited by a moderator:
Ok well done but what made you think and how did you work out or find it was back emf I've always been very suspicious of this back feed on the neutral still struggle sometimes to work it out can anyone explain to me in idiot form lol

Back EMF arises whenever current is removed from an inductive load (such as a coil in a larger relay or solenoid). The inductive load resists the sudden change in current and produces a reverse voltage see similar issue here http://www.------.org/forums/forum/messageview.cfm?catid=205&threadid=25823&highlight_key=y)
 
Have to admit I would have struggled with that one well done for thinking it through.

Begs the question? What if the TPNE was feeding two flats and a Hall all on different phases? Same fault tripping the RCD in the imaginary flat?
Ps what was the earthing type?

I cant recall the earthing arrangements bit know for a fact that it was not a TT system
 

Reply to RCD tripping Problem solved in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
267
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
762
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
752

Similar threads

Ok I’ll try this when I’m down
Replies
4
Views
382
In my opinion replacing the consumer unit and waiting to see which RCBO trips is not a good fault finding technique. If the lighting circuit...
Replies
8
Views
675
davesparks
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top