L
leolec
I've had a couple of these jobs now, found a garden shed wired into a ring with appliance flex on one of them - nice job
But the one today is a bit bigger a commercial yard - if it's raining the RCD starts tripping at about 5pm.
So I know I'm looking for and from what he's told me I've got a good idea where - so I'm thinking I need to test the Insulation at that point
Is there anything I should/could be doing?
Who makes a good IP5 upwards CU?
yes. RCD can trip if neutral fault is present. think, if the MCB is off and you get a leakage from N to E > 30mA, then RCD will trip as current in L will be 0, and there will be an inbalance. as spin says, first check would be external lighting. be careful if IR testing a ptotocell in circuit. do a "soft " test , 250v N/E
Laugh....
I must admit the 5pm tripping time does equate to a dawn to dusk sensor.
Very clever Spinlondon, im impressed.
Leolec, please let us know the outcome of the fault, thanks.
(1 gold star to Spinlondon I reckon).
Yes, very good point Ian, infact its probably more likely that a time clock switching a supply on is the cause, rather than the dusk to dawn idea.
A hive of interesting thoughts is this forum.
Thanks.
(im still impressed with your idea spin, and you do decerve a gold star, but I think Ian might decerve 2 gold stars).
Time clock. Yes!
Time activated zoned alarm system could be a possibility as well, but would agree sounds like a timer in the equation.
Would be worth a ramp test to see how much current to trip it and a quick clamp test to know what's already there (before 5pm if poss :p).
RCD tripping - testing for cause
Australia
leolec,
topquark,