bonn1ett

Can anyone offer some advice......

Customer recently moved into property, underfloor heating not working but looks like quite a new install. First problem i found was the switched FCU was faulty that supplies the underfloor heating - replaced that, switched on still nothing illuminating on the thermostat screen? Removed thermostat cover to find all the wires were disconnected form the thermostat terminals (alarm bells ringing now). I tested continuity of underfloor element - was 63ohms which is what it should be according to the manual.

I connected everything up, switched on FCU and the rcd tripped in CU. Disconnected all wires from back of thermostat controller including earth, switched on and rcd stayed on. I then connected the live and neutral incoming only to the back of thermostat control (element and thermostat disconnected still), switched on and rcd tripped? I carried out a ramp test on the rcd and tripped at 18mA........could it be the rcd is too sensitive?
 
ok, but the mat is not affecting the rcd as its tripping with the mat diconnected? With only L and N connected (no load) to thermostat its tripping. When i disconnect everything, cables in free air, the rcd stays on, wouldn't this imply that the cable from the CU through the FCU and up to the thermostat is ok?
 
18mAis a bit low, but there could be a bit of leakage somewhere in the house. ramp test the RCD with no circuits/loads connected. if it still trips at 18mA, i suggest replacement.
 
yes will try that. Ran out of time to carry out more tests, advised customer that probable cause is the rcd and may need replacing but will double check everything else first. Don't want to make customer hand over ÂŁ70-ÂŁ80 for a replacement rcd if that's not the problem! Thanks the advice.
 
yes will try that. Ran out of time to carry out more tests, advised customer that probable cause is the rcd and may need replacing but will double check everything else first. Don't want to make customer hand over ÂŁ70-ÂŁ80 for a replacement rcd if that's not the problem! Thanks the advice.


That's a dammed expensive RCD, who's make is it??
 

Reply to RCD tripping with underfloor heating in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
372
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
938
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

J
The rcd spur being fitted is probably because there wasn't rcd protection of that supply.
Replies
5
Views
440
  • Question
It's the policy on this forum not to give step by step advice. If you have an understanding of wiring requirements you will not have any...
Replies
1
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top