Guys, what, if anything, have I missed?
Problem has apparently existed for over a year. Random tripping, no obvious pattern, but can be at 6am when only a fridge freezer will be operating (the f/f has been disconnected and still tripping occurs). It can go days/weeks and be fine with no tripping.
16th Edition board, RCD covering kitchen sockets, oven and shower. Ramp testing (25ma), tripping times(22.6 & 9.9) all good & individual circuit insulation res figures all good. All connections in the board, at the oven, shower and sockets re-made and checked. No sign of any water in the shower casing. Standing earth leakage with various appliances on, around 3-4ma.
Supply is TNS, Ze 0.19.
Not sure if this is a red herring, but the head is a very old cast iron three phase with ceramic fuses and solid neutral link - 1 phase serving the property I'm checking, second not used and third serving the property next door. The two properties are sharing the main earth (sweated lead). I'm thinking that an issue in the adjacent property may be a factor, but how/what do I check (family in this property are on hols so I've not been able to speak to them)?
Any thoughts/suggestions for further action and/or investigation gratefully received!
Regards.
Problem has apparently existed for over a year. Random tripping, no obvious pattern, but can be at 6am when only a fridge freezer will be operating (the f/f has been disconnected and still tripping occurs). It can go days/weeks and be fine with no tripping.
16th Edition board, RCD covering kitchen sockets, oven and shower. Ramp testing (25ma), tripping times(22.6 & 9.9) all good & individual circuit insulation res figures all good. All connections in the board, at the oven, shower and sockets re-made and checked. No sign of any water in the shower casing. Standing earth leakage with various appliances on, around 3-4ma.
Supply is TNS, Ze 0.19.
Not sure if this is a red herring, but the head is a very old cast iron three phase with ceramic fuses and solid neutral link - 1 phase serving the property I'm checking, second not used and third serving the property next door. The two properties are sharing the main earth (sweated lead). I'm thinking that an issue in the adjacent property may be a factor, but how/what do I check (family in this property are on hols so I've not been able to speak to them)?
Any thoughts/suggestions for further action and/or investigation gratefully received!
Regards.