abdulrahman42

Hi All,

I am a little bit confused, I have just bought a house and the boiler and whirlpool bath are connected together to a 16amp breaker, I know the boiler should have its own supply but this is what I got.

Anyway if the boiler or whirpool is turned on, it trips the RCD. Ive disconnected the boiler and turned the whirpool on and vice versa but still the RCD trips. Ive checked the resistance on the appliances and both are good but they are old and my metre might not be great.

Ive put the supply to a 32 amp breaker just to see if the RCD trips however it doesn't and both work. Im confused about the fact that if there was an earth leakage fault I assumed it would still trip the RCD even on a 32 Amp breaker.

Am I missing anything as I'm not sure what to do next. Please Help.

Regards.
 
Can I just chuck my thoughts in here, it says in your profile that you are a trainee electrician. Obviously, from your posts, you are very unsure of what you are about, so why don't you talk to whoever your trainer/mentor is? can we assume from your nick that you are 42? If so, how are you training?
 

Reply to RCD tripping in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
376
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
944
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

My guess is an earth to N fault in the damaged light fitting. This will become a problem when other devices draw large currents.
Replies
2
Views
350
Seen this where T&E has been fixed with a flat bend of too tight a radius.
2 3
Replies
35
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top