P

pjb1

Did a cu change recently on a domestic property. The Landing light which is on the downstair radial. Keeps tripping the rcd in the consumer unit.Before the change the lamp holder had a energy saving low wattage lamp in it which the owners of the property have replaced with a 60w lamp, and like i've said when they turn it on takes out the board. Is this a case of a borrowed neutral from the upstair radial?.
 
Sounds definately like a borrowed neutral there to me.

Neutral comes off the upstairs lighting circuit with the live pinched off the hall light S/F at the 2g switch at the bottom of the stairs.
 
Should have done a Pir, Created a rod for my own back here. How would this borrowing of the upstair neutral have shown it self during testing?.
Is there anything I am able to do other than start chopping out walls to run a neutral in for the landing light.
 
Last edited by a moderator:
Should have done a Pir, Created a rod for my own back here. How would this borrowing of the upstair neutral have shown it self during testing?.
Is there anything I am able to do other than start chopping out walls to run a neutral in for the landing light.


Put upstairs and downstairs lighting on same RCD and note borrowed neutral on cert.

Yes you should have done PIR before CU change this is always one to watch out for.

I always check by isolating downstairs lighting to see if landing light is on same circuit. Then remove the neutral form the circuit and put it in block connector. Re energise circuit and check to see if landing light comes on. If it does you have a borrowed neutral.
 
Cheers Guys
For the advise should have know better,Once bitten twice shy. As me old mum use to say will you never listen:confused:
 

Reply to Rcd tripping in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
807
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
853

Similar threads

In my opinion replacing the consumer unit and waiting to see which RCBO trips is not a good fault finding technique. If the lighting circuit...
Replies
8
Views
682
davesparks
D
My guess is an earth to N fault in the damaged light fitting. This will become a problem when other devices draw large currents.
Replies
2
Views
343

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top