RCD Tripping | on ElectriciansForums

Discuss RCD Tripping in the UK Electrical Forum area at ElectriciansForums.net

Joined
May 19, 2020
Messages
5
Reaction score
0
Location
Uk
Evening, came across a fault today on a new board that’s been fitted by a previous electrician. Split load dual RCD 6 way Hager board, when a fused spur is switched on or when the boiler starts up the RCD trips but the circuit is on the other RCD. Have checked the all wiring at the DB and all is ok. The previous board was a old wylex 100ma RCD board and never tripped.
 
Borrowed neutral was my thinking. However the previous electrician fitted a single 30ma RCD board before this board and it still tripped. Earth leakage is too high for a 30ma RCD, but why would the other rcd trip and not the rcd protecting the circuit?
 
Evening, came across a fault today on a new board that’s been fitted by a previous electrician. Split load dual RCD 6 way Hager board, when a fused spur is switched on or when the boiler starts up the RCD trips but the circuit is on the other RCD. Have checked the all wiring at the DB and all is ok. The previous board was a old wylex 100ma RCD board and never tripped.
I had a similar problem couple of years ago. RCD2 was tripping whenever any load was put on kitchen ring baffled me. I carried out insulation resistance test and found that the fault was on the downstairs lights which was on RCD1 screw touching neutral in living room light. It was also a Hager split load board. Do an IR test on circuits that will find the fault for you.
 
Had a fault similar to this about a year ago and the fault was on one of the circuits off the RCD that was tripping, had me puzzled for a while especially when I did an RCD test on the incoming side of the RCD's and it tripped the RCD, fault was found using a cable locator to be a floorboard nail partially through a cable
 
N-E fault could be on one of the circuits that is on the RCD side that is not tripping. take the suspect N's out of bar and IR test.
 
Yes a N-E fault, I had that many years back with a pinched neutral in a double socket, I admit it was a socket I had installed. can't find the embarrassed emoji, so ?
 
So yesterday the owner disconnected a lighting circuit from the side that tripped and everything worked fine, didn’t trip once.
my tester is being calibrated at present once it’s back I will carry out the tests.
 

Reply to RCD Tripping in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
376
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
944
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Seen this where T&E has been fixed with a flat bend of too tight a radius.
2 3
Replies
35
Views
1K
  • Question
Thank you for taking the time to help explain this - much appreciated
Replies
7
Views
866

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top