It looks like the MCB labelled "RCD" on the top board is feeding the bottom board.
Start but switching off all of the MCB on the bottom board. Then try resetting the MCB on the top board and see if it stays on at this point.
Then see if you can reset and trip-test the RCD on the bottom board (the RCD is right-most and double the width of the MCBs). The RCD should have a small 'test' button to verify it goes OK.
If you can reset the top MCB, and the RCD tests OK and stays on, then try switching on each of the bottom MCB in turn, waiting a minute or so between them in case the fault is not "instant".
Hopefully you will find which circuit is faulty that way. Once you find it, leave that MCB off and reset to the top MCB and RCD to get the rest of the power on.
You will need to get someone in to fix it unless you can identify a faulty appliance that is causing it, even then you are probably best to get some help. If you can post your town/post code (but no personal details) then someone on this forum might be able to come out and can send you a personal message.