M

matt12321

ive got an rcd that keeps tripping on a split load board. circuits 3 ring mains, 3 lighting circuits and 2 boilers. insulation tests come back greater than 1M on all circuits, what else could it be, faulty appliance, rcd? what else could i look for
 
why not try isolating all final circuits at the C/U....then reset the RCD.....make sure that all connected loads on final circuits are on....then reinstate supply on each circuit in turn....until the rcd lets go......that will give you a start......oh and by the way...did you test strappers for 2 way lighting in BOTH directions when conducting an IR test?....
 
thats the first thing i tried thanks glennnspark and yeh strappers tested. intermittent fault as all circuits turned back on individually and no individual circuit trips the rcd, it will trip at random times
 
insulation tests come back greater than 1M on all circuits,
If I were getting multible circuits with reading around 1M or only slightly greater then I would be concerned. 2 circuits at 1M drops that too half straight away.. and with that nuesance tripping begins...
you say split load. If you cant narrow it down with testing I would be tempted to jump one circuit across and leave it a few days and see if it continues.. keep doing that till the circuit that trips has been swoped and the tripping stops... a cheat way out and takes time, but will help narrow it down

edit to say I dont mean leave it on the non rcd side forever just use that to find the fault
 
Last edited by a moderator:

Reply to rcd tripping in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
265
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
756
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
746

Similar threads

  • Question
Thank you for taking the time to help explain this - much appreciated
Replies
7
Views
852
  • Question
I would add though that a typical good TT rod of 100 ohms only needs 3V to have 30mA flowing and so trip an RCD, you might find that sort of N-E...
Replies
8
Views
680

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top