Hello guys had a lady on the phone who said she has upstairs and downstairs ring mains, she can plug the 1400 watt vac in upstairs and its fine but she cant plug it in downstairs as it trips the RCD protecting it I am not sure never come across this?
 
Could just be that one RCD is more sensitive than the other. Tests will show.

Either way, sounds like the Vacuum sucks.
 
This is becoming a more recurrent theme: nuisance RCD tripping through nothing more than electrical accumulation. I'll often clamp a 'perfectly good' domestic installation's tails and see the other side of 40mA+ leakage, through all the digital stuff plugged in.

What's the betting that next set of regs will have us all installing RCBO's and doing away with the split board??
 
Yes accumulation of leakage is becoming a large thing now, as you say all these digital appliances its not rare to see high leakage. I find where possible to use Rcbos they are so much better but the price of a loaded rcbo board doesn't bare thinking about!
 
Yes went round to look the kitchen and living room are on one ring main downstairs and upstairs is on another now everything works fine except when youplug the vacuum into a socket in the living room it trips the RCD but plug it into the kitchen it also works fine, the vacuum is 1400 watt dyson but plug the kettle (2300 - 3000 W) into the living room sockets and it works fine not come across this in the forces I tell you. The installation is on a split double RCD board.
 
Last edited by a moderator:

Reply to RCD Tripping in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
257
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
739
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
721

Similar threads

  • Question
Hi Gingerrubix, The fact that your previous Tenant replaced a faulty socket plate which he used for an external EV, raises an eyebrow. Also your...
2
Replies
25
Views
3K
  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top